Disabled handrails not continuous around the external perimeter....

  1. 4,987 Posts.
    lightbulb Created with Sketch. 392
    Disabled handrails not continuous around the external perimeter. the internal handrail also does not appear to comply with AS1428.1
    Gaps under glass and at the end of the balustrade greater than 125mm
    Chair rail encroaches into the minimum 1m unobstructed width of the stairway
    The nosings and stairs do not provide the required slip resistance
    The nosing strip is not continuous along the width of the stair
    The nosing strip does not provide 30% luminance contrast against the blue stair
    Nosing strip not required on the intermediate landing
    There is a chair on the intermediate landing. Most likely not permissible if this stair is a required-non-fire-isolated stairway

 